Quote:
Originally Posted by PaulInTheSticks Ethan,
For comparing the soundproofing affect of cellulose vs fiberglass, there is no comparison. |
The test you linked to is meaningless.
The only thing that's meaningful is a lab test using comparable wall construction.
Probably the most extensive testing done on isolating assemblies were those performed by the National Research Council Canada (NRC)
In their publication IR-761 they tested over 350 wall assemblies - and they did this strictly for the data - not to promote any particular product - so this is as unbiased a set of results as you will ever find.
In their tests numbered TL-93-313 (sprayed cellulose insulation) and TL-93-283 (fiberglass insulation) you can compare 2 otherwise identical wall assemblies - 2x4 framing - 24" on center - 1" air space between inside faces of framing double layers of 5/8" type X drywall on each face - wall samples were 8' high by 10' wide.
Here's the results (TL values for the sprayed cellulose are the ones on the left):
TL-93-313(STC 66) TL-93-283 (STC 69)
Frequency...TL........TL
50 Hz.......30.0......26.7
63 Hz.......21.0......31.8
80 Hz.......28.8......36.6
100 Hz......37.0.....39.5
125 Hz......44.4.....44.6
160 Hz......48.3.....51.3
200 Hz......51.9.....55.9
250 Hz......55.7.....61.8
315 Hz......57.2.....64.9
400 Hz......60.3.....67.3
500 Hz......64.8.....70.1
630 Hz......67.2.....72.9
800 Hz......71.3.....78.0
1000 Hz....75.3.....81.5
1250 Hz....79.8.....85.6
1600 Hz....81.4.....83.9
2000 Hz....75.5.....75.3
2500 Hz....75.5.....75.9
3150 Hz....82.1.....81.7
4000 Hz....88.1.....87.4
5000 Hz....92.2.....91.5
6300 Hz....91.1.....90.7
Now - the overall advantage lies with fluffy fiberglass insulation in this case - sure you get a small boost with cellulose at 50Hz (3.3dB) but then take a huge hit in isolation at 63Hz (-10.8dB).
When you look at the numbers as a whole - it simply makes no sense whatsoever to bother with anything other then the cheapest material you can put in the bay - which is fiberglass.
If you wish I could post the same comparison for fiberglass versus blown cellulose insulation - but I'll let you know in advance that I used spray cellulose right off the bat because it performed better then the blown did in the comparison.
I would also point out that there has to be some concern with blown as to the possibility of it settling over time - as it does the TL values will decrease, perhaps dramatically.
According to the video you linked to - there would be a clear advantage to making use of cellulose of roughly 33dB weighted - that is huge - yet we don't see it when we look at real world test results (in fact we see a 3dB weighted benefit to the fiberglass).
You can (of course) use whatever you wish to use - perhaps "green" is your motivating factor - in which case go green and settle for less isolation over all - there is nothing wrong with that if that is your choice - but don't buy into the bullshit hype you find on you-tube - at least use real data to base the decision on.
Rod