Quote:
Originally Posted by Jedanor It will depend on the allowable amount of static pressure drop the system can handle. |
Sadly I don't have that information. Have to talk to the developer of my building to get it, and he's on vacation.
Quote:
Originally Posted by Jedanor There are silencers on the market (google IAC LFS) capable of providing in excess of 15 dB dynamic insertion loss at low frequencies (63 Hz). The tradeoff is significant increase in pressure drop to your system. Bear in mind if the system operates more inefficiently it may produce more noise than you have now, so this is also a tradeoff. |
Are you talking about something like this:
http://www.industrialacoustics.com/u...prod%20lit.pdf
It's a silencer that attenuates 6db @31.5hz, 16db @63hz, 32db @125hz and 46db @250hz for an air velocity of -1000 fpm.
But it's '10 long... is this the rule, that to get any substantial low frequency reduction you have to use really long silencers? How do muffle/baffle/attenuation boxes at the intake and outtake compare, spec wise?
Description of a design Rod suggests here:
Why do I need roof ventilation?!
Picture of a design he suggests:
HVAC Baffle Box Construction Plans
(Picture of similar type of box attached.)
Quote:
Originally Posted by Jedanor What are you using the room for where you need low frequency isolation from silencers? That will help assist in providing your solution, assuming you need one. |
I need to reduce noise leakage via the ventilation ducts to the neighbours from a tracking/mixing room yet to be built. Sound attenuating solutions both inside and outside the tracking room is an option.