Nothing in the search that discussed the actual wiring of the Variac for dimming lights. I play single coil guitars most often and this is crucial.
I have 14/2 Type NM (romex). Power to existing switch comes from the fixture.

OK, so I understand how the Variac would be wired traditionaly.

Input: Hot (black) to terminal 2, Neutral (white) to terminal 4

Output: Hot(Red) terminal 3, Neutral (white) terminal 4

I was sitting here and I realized that all I have is 14/2 (still need to verify tonight) in my switch location. I marked the White (normally neutral) beacuse I'm using it as a Hot to the switch (again power from the fixture). To make matters worse I have already hung 5/8" type X in the ceiling and on soffits above switch. The wall is still open.

So heres my question: If I were to keep my existing set up with the "marked" hot coming to terminal 2, my black Hot to terminal 4 than all I'm missing is the Neutral right? So would tapping into the neutral from another light fixture allow the Variac to function properly? My (ignorant) logic here is that the voltage drop shoud "occur" on the Hot conductor, and the neutral is already @ the light fixtures themself.

Maybe I'm chasing my tail and need to just start taking down drywall. I hope not.

Thanks in advance for any suggestions from those with this type of knowledge.
soulfield is offline  
Reply With Quote
Old 4th February 2011   #2
Gear Guru
 
tINY's Avatar
 
Joined: Jul 2004
Location: Orygun
Posts: 11,123



Hard to say without a diagram.

It may be worth $100 to get an electrician out to do it right....



-tINY

tINY is online now  
Reply With Quote
Old 4th February 2011   #3
Lives for gear
 
jhbrandt's Avatar
 
Joined: Feb 2009
Location: Jakarta, Indonesia
Posts: 2,945

Send a message via Yahoo to jhbrandt Send a message via Skype™ to jhbrandt
Quote:
Originally Posted by soulfieldstudios View Post
I was sitting here and I realized that all I have is 14/2 (still need to verify tonight) in my switch location. I marked the White (normally neutral) beacuse I'm using it as a Hot to the switch (again power from the fixture). To make matters worse I have already hung 5/8" type X in the ceiling and on soffits above switch. The wall is still open.
You do not have a neutral in that box & according to NEC the white wire should have been taped with black tape to indicate a 'hot' switch circuit.

Quote:
Originally Posted by soulfieldstudios View Post
So heres my question: If I were to keep my existing set up with the "marked" hot coming to terminal 2, my black Hot to terminal 4 than all I'm missing is the Neutral right? So would tapping into the neutral from another light fixture allow the Variac to function properly? My (ignorant) logic here is that the voltage drop shoud "occur" on the Hot conductor, and the neutral is already @ the light fixtures themself.
NO. Do not do that.

As tINY suggested, get an electrician in there to do it right. You could risk burning the place down. -- You will need to run the power up from where the switch is and feed the light circuits from the variac.

Good luck!
Cheers,
John
__________________
John H. Brandt
Recording Studio Design/Consulting, Acoustics, & Electronics
Jakarta, Indonesia
See our new PRODUCTS page.

"Twenty thousand dollars worth of Snap-On tools does not make you a Professional Diesel Mechanic"
jhbrandt is offline  
Reply With Quote
Old 4th February 2011   #4
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
Looked last night after work and i have 14/3 in to the box.

At this point all I can do is run a second line of 14/2 back to the first light fixture and re-wire the fixture so that the incoming power goes directly to the switch > Variac | then the new dedicated run > back to the fixtures.

My prior post was def a bad idea once I really thought about it.

This build has been a one man crew all the way from framing, MEP, and Gyp Board to finish and casework. No budget for outside help. I am confident with electrical but have never wired a variac before.
I wired the rest of the studio CR, LR, bath, den, and Ejector pump based upon the IRC + NEC, and think I have this right.

So incoming power

> Hot (black) to Switch > to Variac terminal 2
> Neutral (white) > to Variac terminal 4

Ground > Ground

Output

> Hot (Black) > from variac terminal 3 > to Fixture
> Neutral (white) > from variac terminal 4 > to Fixture

Ground > Ground

Right?
soulfield is offline  
Reply With Quote
Old 4th February 2011   #5
Lives for gear
 
avare's Avatar
 
Joined: May 2004
Location: Hamilton, On Canada
Posts: 4,445

Quote:
Originally Posted by soulfieldstudios View Post
OK, so I understand how the Variac would be wired traditionaly.

Input: Hot (black) to terminal 2, Neutral (white) to terminal 4

Output: Hot(Red) terminal 3, Neutral (white) terminal 4
Which model Variac is it? On the 100/200 series the input is neutral terminal 1 and hot terminal 4, assuming you are not loking for any voltage boost.

St100 200 Wiring

Andre
__________________
Good studio building is 90% design and 10% construction.
avare is offline  
Reply With Quote
Old 7th February 2011   #6
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
Its a staco 501 5A 120v

No boost just dimming about (15) 30w halogen GU-10.

I do not have the variac in hand yet to confirm wich terminal is which on this particular unit. All the bad weather in memphis and the mid west slowed FedEx alot so hopefully I will have the unit today and will confirm the terminal layout.

I finally bit the bullet and removed some of the 5/8 type X gypsum on the ceiling and soffit, and snaked my second run of romex from the switch/Variac location to the first light fixture it will control.

Once I get the unit in hand I will have to figure out what enclosure I want to use or modify in order to wall mount the Variac and Switch.

I know I couldnt find alot when I started searching for wiring Variacs so I plan to photograph and maybe scetch a schematic of my install to help others in the future.

Fingers crossed for Fed Ex to deliver today. stike
soulfield is offline  
Reply With Quote
Old 7th February 2011   #7
SAC
Registered User
 
Joined: Dec 2009
Posts: 2,622

LED Dimmer

Its a pretty good article that illusterated the proper way to effectively dim LEDs.

Gee, I wonder why they have electricians? As with so many who know more then they do their market should be exponentially sinking due to the impact of Darwin's postulates.

http://www.ledsmagazine.com/features/1/12/6
SAC is offline  
Reply With Quote
Old 7th February 2011   #8
Lives for gear
 
avare's Avatar
 
Joined: May 2004
Location: Hamilton, On Canada
Posts: 4,445

Quote:
Originally Posted by soulfield View Post
Its a staco 501 5A 120v

All the bad weather in memphis and the mid west slowed FedEx alot so hopefully I will have the unit today and will confirm the terminal layout.
There are 501C, and 501-C models. The conections are shown on the drawings.

501C
501-C

Andre
avare is offline  
Reply With Quote
Old 7th February 2011   #9
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
SAC - Excellent read. I wish the budget for my build would allow for LED lighting.

ANDRE - Thanks for the schematics! These are much more legible than the ones from Mosier's website.

It is indeed a 501C. My first take is the same as I thought with one change

Terminal 5 being input (hot)

Terminal 4 being common (neutral)

Terminal 3 being the output (Hot to fixture)


Also appears that you can easily reverse the clockwise attenuation to counterclockwise by interchanging terminal 5 to terminal 2 (hot), and terminal 4 to terminal 1 (common / neutral)

I will need to study this a little further tonight.

Would you believe FedEx didnt make the delivery today!

Sucks because I work better when I'm holding the unit than I do planning on paper. As an unlicensed (not yet eligible) Architect you'd think I would be able to lay this stuff out on paper.

I guess tomorrow night after rehearsal for the Album release party, I will get to install this bad boy! (Assuming FedEx does there part)

Thanks again Slutz
soulfield is offline  
Reply With Quote
Old 8th February 2011   #10
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
At last the Staco 501C Variac arrived this morning. I will say its a beautiful piece of gear. While it only weighs 5 lbs, it feels like 10!

Now to devise the mounting and get this thing up and running.

I will post pics, schematic, and a short synopsis of the install once completed so that others searching can see some real information on Variacs and incandescent light dimming.

My butterscotch american strat is already happy about this one.

Give me a few days.
soulfield is offline  
Reply With Quote
Old 10th February 2011   #11
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
Variac Installed

Variac is now installed and I am stunned with the results. Took a little DIY to get the enclosure right. I modified a 6" x 6" x 4" type 1 Nema enclosure
so that I would have an accessible but rigid enclosure. Remember this unit weighs 5.4 Lbs.


Here is a picture of what the 501C looks like.



Also attached is a picture (blackberry pics suck) of the installed Variac + Enclousre and mounting.





The first thing I did was install my second run of 14/2 from the enclosure location to the first light fixture. This gave me two runs:

14/2 Run A - Power from breaker (hot from this passes through a simple light switch before the input of the Variac.)

14/2 Run B - Output from Variac to first light fixture


Second, I mounted the enclosure and brought Run A & B into the enclosure.

Third, I traced the template provided with the unit on the cover for the Nema enclosure and drilled holes for the shaft and mounting bolts. Also before mounting the enclosure I drilled holes for the entrance of the input A and output B. These had to be cleaned with a little wire brush dremel action. After all the burrs were removed I installed gromets to protect where Runs A & B enter the top of the enclosure

I mounted the variac on the cover plate of the enclosure.


Forth, I shut off the power to this dedicated lighting circuit.

After careful review of the Schematics that Avare was nice enough to provide and the limited documents that came with the variac I made the following connections. (WARNING! these connections are specific to the model I have. Anyone installing a Variac should be sure to verify the function of the terminals on the unit they are installing as they can be diffrent from one model to the next)

Ground to Ground for both Run A + Run B

Input Run A (post light switch) Hot (black) to terminal 1
White (Neutral) to terminal 4 (common)

Output Run B Hot (black) to terminal 3
White (Neutral) to terminal 4 (common)


One item to note. This unit has 2 input terminals. Per the schematic terminal 5 is for over voltage and will provide the output with max 117% of the input. Using terminal 5 could output up to 140v which is not a good thing for halogen bulbs.

Terminal 1 is for Line voltage which is what I needed for my scenario, and this will provide the output of max 100% (120v) of the input.

TEST - Turned the breaker back on and tested the unit. Glorious light of all levels. No noise what so ever. The strat and never picked up a thing.

I ecpected this unit to create a fair amount of heat and I even provided additional holes for ventin top and bottom. To test this I ran the unit at approx 30% of input for 3 hours and the Nema enclosure was still cold to the touch.

I only have temp keyless light fixtures inplace until the drywall work is finished but it is really awsome to see the various light levels all the way down to a barely glowing incandescent filament.

I hope this little synopsis will help anyone curious about uisng a Variac to Dim 120v lighting.

Now back to having fun hanging 5/8" type X
soulfield is offline  
Reply With Quote
Old 10th February 2011   #12
Lives for gear
 
avare's Avatar
 
Joined: May 2004
Location: Hamilton, On Canada
Posts: 4,445

Congratulations on a great lighting control install. Thanks for the details of the install and the report on the results. It is difficult to explain to those who have experienced it, the beauty of continous variable lighting from off to fully on.

Of course what is also often overlooked in studio applications is the insignificant electrical noise created. Variacs are expensive compared to almost all electronic dimmers, but when you need the characterstics of a variac, it is worh it.

Andre
avare is offline  
Reply With Quote
Old 10th February 2011   #13
Lives for gear
 
PaulP's Avatar
 
Joined: Sep 2009
Posts: 1,196

Interesting thread, thanks for sharing.

The more I wait to start work on my place, the more great ideas I'm going to be able to include.
PaulP is offline  
Reply With Quote
Old 10th February 2011   #14
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
Thanks AVARE!

Paul,

I hope this will give you a jump start when planning the lighting for your place.

I'm about 75% of the way through my build (promise I will get a photo thread of the build one of these days) and although I planned and planned, things always seem to change once your building and making decisions on the spot.

Apparently I did not plan enough in the begining and the Variac was a perfect example. Mind you I only back tracked 2 pieces of 5/8" Gyp and a little extra romex, but I should have planned this out before hand.

Good luck with the plan/build work ahead paul
soulfield is offline  
Reply With Quote
Old 11th February 2011   #15
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter


The enclosure is about flush with the edge of drywall and I plan to make a stained wood panel that will be hinged and trimmed out to match the mic line panel.

Very happy to see this wall completed and the variac is helping me feel like this will one day be a finished studio.
soulfield is offline  
Reply With Quote
Old 11th February 2011   #16
Gear maniac
 
soulfield's Avatar
 
Joined: Jul 2005
Location: Dahlonega, Georgia
Posts: 261

Thread Starter
Some tips I forgot to include for anyone doing a similar enclosure.

1. The terminals on these Staco Variacs are fragile. I didn't have any problems but use caution not to put stress on the terminals.

2. The 6x6x4 enclosure was just large enough for the 501C. That said tuck your wiring neatly. The first time I placed the unit I had a wire nut in the back of the enclosure that was rubbing the back of the Variac as it turned.

3. Protect the windings on the Variac. The edges of the enclosure were rather sharp and its almost impossible to place the unit without touching the copper windings on the edge of the enclosure @ some point. I placed two layers of electrical tape to pad this contact.

4. When you trace the template oversize the hole for the shaft. The schematics call for 7/16" hole with a 3/8" Variac shaft. I used 1/2" for the hole which gave just a little wiggle room.

Just trying to contribute something back to the forum that has provided me with so much valuable information.

Thanks guys!
soulfield is offline  
Reply With Quote
Old 9th October 2012   #17
Gear maniac
 
Joined: Nov 2009
Posts: 160

Soulfield's wiring advice pictured below. Worked great for me too. Thanks, soulfield, really appreciate it.

The one thing I would add is that the 6" x 6" x 4" type 1 Nema enclosure is a bit tight. You might want more room to accommodate the wiring, as the Dial Plate is located at the back of the 501C.

Andy_R is offline  
Reply With Quote
New Reply New Reply Submit Thread to Facebook Facebook  Submit Thread to Twitter Twitter  Submit Thread to LinkedIn LinkedIn 

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Similar Threads
Thread Thread starter Forum Replies Last Post
Studio Electrical Wiring and Power conditioning migsoto Studio building / acoustics 20 18th October 2011 01:45 PM
Bringing up voltage on a Variac John Noll Geekslutz forum 12 28th July 2010 10:43 PM
Electrical scheme (wiring diagram) for the Audio Technica AT4033a microphone exists ? MrTNT Low End Theory 0 27th August 2008 01:31 PM
Dealing with holes in the wall from electrical outlets/wiring nd33 Studio building / acoustics 8 3rd July 2008 08:10 AM
Variac Before the Amp morebutter So much gear, so little time! 11 3rd June 2008 03:42 PM


All times are GMT +1. The time now is 12:01 AM.

Home - Search Forum - Contact Us - Terms Of Use / Privacy Policy - Advertise on Gearslutz - All Advertisers - Top
 
 
Powered by vBulletin®
Gearslutz.com LTD - UK Company Number 7597610.
Registered Office - 35 Ballards Lane, London, N3 1XW.
Hosted by Nimbus Hosting.

By using this site, you agree to our use of cookies.

SEO by vBSEO ©2011, Crawlability, Inc.