So, we are changing our control room ratio.
Right now it is (LWH) 26.75'x13'x10.75' (1 : 1.21 : 2.49)

I can't change the width or the height of the room.

According to Ethan's Room Mode Calculator, the closest that I could get to one of the "recommended ratios" is shortening the length to 17 feet.
This would give me a ratio of (1 : 1.21 : 1.58)

After playing around with the calc, I thought that 19.5 feet looked pretty darn good. 20.5 feet looked ok, too, but is a multiple of the height, which I always thought was a no-no. Maybe I'm reading the calculator wrong.

Which length (17, 19.5 or 20.5) should I go with and (if you have time) why.
Please assume that the room is untreated.

As a side question, my partners want to make the new wall (which would be the front wall) angled so that it wouldn't be parallel to the back wall.
This doesn't feel like a good idea to me, but I'm not exactly sure as to why...

Thank you all for the time.
Seamus
__________________
Seamus
Upstate New York
Seamus TM is offline   Reply With Quote
Old 21st February 2009   #2
Gear nut
 
Join Date: Nov 2007
Posts: 87

Seamus,

The best length dimension in your case would be 20.425 ft. This is a ratio of 1.9/1 with the height dimension, and a ratio of 1.57/1 with the width dimension.

This is your best bet because 1) it is always best to stay within the octave (2/1) for all three dimensions, all else being equal, and 2) it is the golden ratio between the two largest dimensions, which is pretty hard to beat. (The only two ratios that are as good or better in some cases are 1.26/1, or the square root of the golden ratio, and 1.4/1, the square root of two.)

Incidentally, your ratio of 1.21/1 is also a good one - a minor third. So your room will be an augmented major seventh chord with no third degree. Pretty hip...no perfect intervals...

Wes

Wes Lachot Design || Studio Design and Acoustic Consulting
__________________
WES LACHOT DESIGN
Wes Lachot is offline   Reply With Quote
Old 21st February 2009   #3
Moderator
 
jayfrigo's Avatar
 
Join Date: Dec 2002
Posts: 3,352

Agreed with Wes. Remember, there's more than just the ratio to consider. If you have a few that look good, consider other factors and don't blindly clint to a single criterium in a cognitive vacuum. 17" deep is pretty small, so even if that ratio had looked a tiny bit better, you probably would have wanted to pass on it for other reasons.

Where will you sit in the room to avoid problematic nodes and/or antinodes, especially the room's center? What gear do you need to fit? Are the monitors free standing? Do you want to be able to use diffusion in back? Will clients be in attendance? With all these things taken into consideration, you'd probably pass on 17, no matter how good the math looks. Also remember that with enough treatment of the proper kind, any reasonably good ratio can work just fine. It's not like there is one, and only one possibility to the exclusion of all other factors.
__________________
Jay Frigoletto
Mastersuite
www.promastering.com
www.studiometronome.com
jayfrigo is offline   Reply With Quote
Old 21st February 2009   #4
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Thanks, guys.
I was hoping that 17 feet was not the answer for the reasons that Jay suggested.
Too small.

What about making the new wall not parallel with the back wall?
I feel like it's more trouble than it's worth and could introduce bigger problems than we already have.
Keep in mind that the wall that we are constructing will be the front wall.
Seems like a bad idea.

Thanks, again,
Seamus
Seamus TM is offline   Reply With Quote
Old 21st February 2009   #5
Lives for gear
 
nosebleedaudio's Avatar
 
Join Date: Jun 2005
Location: Birmingham, AL USA
Posts: 3,547

Send a message via AIM to nosebleedaudio
Quote:
Originally Posted by Mumblesound View Post
Thanks, guys.
I was hoping that 17 feet was not the answer for the reasons that Jay suggested.
Too small.

What about making the new wall not parallel with the back wall?
I feel like it's more trouble than it's worth and could introduce bigger problems than we already have.
Keep in mind that the wall that we are constructing will be the front wall.
Seems like a bad idea.

Thanks, again,
Seamus
Which direction would you slant?
Could make things worst..
I would not worry about parallel, symmetry is very important as well...
People think that any wall being parallel is the kiss of death...
Treatment is your friend.. but it also depends on other things..
A well designed room requires time and experience, no substitute for either one...
__________________
Mike Keith
www.jmkaudio.com
nosebleedaudio is offline   Reply With Quote
Old 22nd February 2009   #6
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Thanks, everyone.

Sounds like I'll make it 20.425 and parallel to the back wall.

Seamus
Seamus TM is offline   Reply With Quote
Old 23rd February 2009   #7
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
One more hair-brained question.

There is a very large room behind the control room that is just storage.
I am able to take the back wall of the control room totally out and it would open up into this room.

My question is, would it be nuts to take that wall down and replace it with 6-10 feet of velocity trapping (705)? In my head, it would be like there was no back wall at all... would that be a good thing?
In reality, the back wall would be about 75 ft away from the front wall.

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
Old 23rd February 2009   #8
Gear Guru
 
Ethan Winer's Avatar
 
Join Date: Oct 2002
Location: New Milford, CT, USA
Posts: 12,050

Lightbulb

Quote:
Originally Posted by Mumblesound View Post
it would be like there was no back wall at all... would that be a good thing?
Probably!
Ethan Winer is offline   Reply With Quote
Old 23rd February 2009   #9
Gear Guru
 
Glenn Kuras's Avatar
 
Join Date: Jul 2005
Location: Atlanta, GA
Posts: 11,003

Quote:
My question is, would it be nuts to take that wall down and replace it with 6-10 feet of velocity trapping (705)? In my head, it would be like there was no back wall at all... would that be a good thing?
In reality, the back wall would be about 75 ft away from the front wall.
If you do that use less dense fiberglass. The fluffy stuff would work just fine. BTW that would be ONE THICK BASS TRAP!
__________________
Glenn Kuras
GIK Acoustics USA
GIK Acoustics Europe
770 986 2789 (USA)
+44 (0) 20 7558 8976 (UK)

See the NEW Soffit Bass Trap
Glenn Kuras is offline   Reply With Quote
Old 23rd February 2009   #10
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
So, I wouldn't need to buy 800 cases of 4" 705?
That's a good thing.

If I just used the fluffy, how deep do you think I should go for it to be worth it?

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
Old 24th February 2009   #11
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
So, I can only really do a 6' x 8.5' section of the entire 13' x 10.75' back wall with the massive bass trap idea.
It's right in the middle of the wall.

That would leave a 2.5' border of actual wall up the sides and along the top.

Still worth trying?

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
Old 24th February 2009   #12
Gear nut
 
Join Date: Nov 2007
Posts: 87

Quote:
Originally Posted by Mumblesound View Post
My question is, would it be nuts to take that wall down and replace it with 6-10 feet of velocity trapping (705)? In my head, it would be like there was no back wall at all... would that be a good thing?
In reality, the back wall would be about 75 ft away from the front wall.

Thanks,
Seamus
Seamus,

No, it would not be better to do that. If you need proof that massive basstraps many feet thick are not the answer for the back of a control room, just take a trip to Nashville where you can hear plenty of rooms built along those lines. Typically, when you sit on the couch in these rooms, a kick drum sounds like it has the EQ of a pencil on a shoebox. Not the way a kick drum should sound, and quite misleading to the listener.

If you play your cards right, 12-16" of velocity trapping will keep your head close enough to the rear wall to actually hear some bottom end. And anyway, why would you want to take those nice ratios I turned you on to and just toss them aside? Maybe I didn't charge you enough...

--Wes
Wes Lachot is offline   Reply With Quote
Old 24th February 2009   #13
Moderator
 
jayfrigo's Avatar
 
Join Date: Dec 2002
Posts: 3,352

Quote:
Originally Posted by Wes Lachot View Post
No, it would not be better to do that. If you need proof that massive basstraps many feet thick are not the answer for the back of a control room, just take a trip to Nashville where you can hear plenty of rooms built along those lines. Typically, when you sit on the couch in these rooms, a kick drum sounds like it has the EQ of a pencil on a shoebox. Not the way a kick drum should sound, and quite misleading to the listener.
Agreed that a massive trap as described is not the best answer here, but that doesn't mean some manner of sizable trapping in the rear of a control room isn't a valid and very workable approach in the right application. Using some of that space for trapping may be appropriate if designed right, but as always, it needs to be part of the whole room plan, and you can't simply open up a huge amount of space, moving the structural boundary back (essentially moving the wall), and maintain the ratio's predicted effects.

Re: the low end response in the rear of the room, I hate how the couch in the back of most control rooms is a boomy mess with unrealistic bass reinforcement. You don't need a wall behind you to hear big bass from a kick drum in a good room with good monitors. If the pressure wave passes you before getting trapped behind you (as much as is possible from a few feet of fiberglass), you will hear it, variables such as proximity to nodes/antinodes (areas of constructive and destructive interference due to boundary effect) and monitoring issues not withstanding of course.

I suppose what I'm saying is that there is some middle ground. The primary seating area for the engineer is most important, but the client often listens on the couch, so it shouldn't be ignored, whether too bassy or too dry. One or two of those Nashville rooms sound OK too, BTW. The good ones don't put the couch in the middle of a nasty node due to the depth of the trap in relation to the actual structural depth of the room. There are good and bad examples to be found of many techniques.
jayfrigo is offline   Reply With Quote
Old 24th February 2009   #14
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Wes:

OK, OK! Uncle!
After thinking some more about it, I could see how the idea might be useful if I needed to fire down the width of the room, as opposed to the length... maybe..I guess... right? (don't hurt me, I'll give you my milk money).
Since my room is pretty narrow, it would probably cause more problems than it helped.
On a side note, I just noticed how many posts you have. You are a very welcome addition to this forum. Thanks for being here.


Jay:
Understood, agreed and thank you.

Seamus
Seamus TM is offline   Reply With Quote
Old 24th February 2009   #15
Lives for gear
 
Weasel9992's Avatar
 
Join Date: Jun 2006
Location: Savannah, GA
Posts: 4,339

Send a message via AIM to Weasel9992
Quote:
Originally Posted by Wes Lachot View Post
Seamus,

The best length dimension in your case would be 20.425 ft. This is a ratio of 1.9/1 with the height dimension, and a ratio of 1.57/1 with the width dimension.

This is your best bet because 1) it is always best to stay within the octave (2/1) for all three dimensions, all else being equal, and 2) it is the golden ratio between the two largest dimensions, which is pretty hard to beat. (The only two ratios that are as good or better in some cases are 1.26/1, or the square root of the golden ratio, and 1.4/1, the square root of two.)

Incidentally, your ratio of 1.21/1 is also a good one - a minor third. So your room will be an augmented major seventh chord with no third degree. Pretty hip...no perfect intervals...

Wes

Wes Lachot Design || Studio Design and Acoustic Consulting
Great post. Welcome aboard Wes!

Frank
Weasel9992 is offline   Reply With Quote
Old 24th February 2009   #16
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
This is not sucking up.
I just checked out your web site, Wes, and all I can say are words like "wow" and "inspiring".

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
Old 25th February 2009   #17
Gear nut
 
Join Date: Nov 2007
Posts: 87

Seamus,

Thank you very much.

By the way, your 20+ ft. deep room will be nice for monitoring. I've found that if you monitor a couple of feet forward of the midpoint of a 20 ft. deep room, the 12 ft. distance from the back wall puts you in the 1/4 wavelength null point of 24 Hz or so, a very acceptable frequency for a null since it's all but inauduble anyway. The biggest thing you have to worry about then in terms of rear wall reflections is the 3/4 wavelength null (72 Hz). We use tuned traps to combat these type of nulls.

Rooms that are much less deep move the 1/4 wavelength null up unto the 30s and 40s where it really hurts the bottom end. That's fine for certain production tasks, but for critical mixing, a 20 ft. deep room is pretty deluxe.

--Wes
Wes Lachot is offline   Reply With Quote
Old 25th February 2009   #18
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
A-ha.
That's great info.

I suppose that rooms that are deeper than the 20 ft would be fine at the 1/4 wave but the 3/4 wave would start to move down, as well, making it more difficult to treat... right?

So, would that be based on the speakers being pretty close to the front wall?
I noticed that you use a lot of soffit designs in the studios that you work on.

Thanks again, Wes.
Seamus TM is offline   Reply With Quote
Old 26th February 2009   #19
Gear nut
 
Join Date: Nov 2007
Posts: 87

Seamus,

Yes, that's right. When you get away from the soffit thing, it gets real complicated fast, because now you are hearing strong reflections from the front wall, and they're louder than h-e-double-hockey-sticks because they're so close to your face. So you get this big huge dip at a fixed frequency (unlike the dip from the back wall whose frequency varies with listener position). The frequency of that response dip is dependent upon the distance of the speaker from the front wall.

The problem with a fixed frequency dip is that it won't go away no matter where you stand (as long as you are between the speakers and the rear wall), so you really start believing it as the real frequency response of the speaker, and hence the mix. So to counteract this response inaccuracy you tend to add back a lot of bass, so that when you take the mix and play it back in a car system, it sounds like mud.

So the upshot of all of this is that I'm a true believer in wall-mount speakers.

--Wes
Wes Lachot is offline   Reply With Quote
Old 26th February 2009   #20
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Quote:
Originally Posted by Wes Lachot View Post
So the upshot of all of this is that I'm a true believer in wall-mount speakers.

--Wes
That's the upshot?
Yikes.

Well, as much as I'd like to, we can't do soffit mounted speakers in our current location... and/or budget, most likely.

I guess that we'll do the old "measure response-move the speakers-measure response-move the speakers" and so on and so forth.

I'm guessing that since the speakers would be relatively close to the front wall, (in my case- somewhere between 0 feet and 8 feet) that the null would be kind of high in the bass range, no?

Thanks again,
Seamus
Seamus TM is offline   Reply With Quote
Old 26th February 2009   #21
Gear nut
 
Join Date: Nov 2007
Posts: 87

Quote:
Originally Posted by Mumblesound View Post
That's the upshot?
Yikes.

Well, as much as I'd like to, we can't do soffit mounted speakers in our current location... and/or budget, most likely.

I guess that we'll do the old "measure response-move the speakers-measure response-move the speakers" and so on and so forth.

I'm guessing that since the speakers would be relatively close to the front wall, (in my case- somewhere between 0 feet and 8 feet) that the null would be kind of high in the bass range, no?

Thanks again,
Seamus
Seamus,

The frequency of the front wall null is computed by taking the speed of sound (1130 ft/sec.) and dividing by 4, then dividing that quotient by the distance between the speaker and the wall. So if the speaker is 7 ft. from the front wall, the null frequency would be 40 Hz, since 1130/4 = 282.5, and 282.5/7 = 40.4.

--Wes
Wes Lachot is offline   Reply With Quote
Old 26th February 2009   #22
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Right-o.
This is where I start to chase my tail.

Would that 40Hz null be "at" the speaker, or "at" the mix position?


By the way, one of my partners is going to Electric Lady, today.
I told him to check out your work.

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
Old 26th February 2009   #23
Gear addict
 
G. E.'s Avatar
 
Join Date: Feb 2009
Location: Austria
Posts: 431

Send a message via Skype™ to G. E.
How to measure the "distance between the speaker and the (front) wall?

Wes,

could you please elaborate on the measurement of the "distance between the speaker and the wall"? Is that the distance from the rear of the speaker or from the driver or the way sound has to pass around the speaker or...?

Many thanks, Gernot
__________________
Gernot EbenlechnerI found a "video" of a song of mine on YouTube
G. E. is online now   Reply With Quote
Old 26th February 2009   #24
Gear Guru
 
Ethan Winer's Avatar
 
Join Date: Oct 2002
Location: New Milford, CT, USA
Posts: 12,050

Lightbulb

Quote:
Originally Posted by G. E. View Post
could you please elaborate on the measurement of the "distance between the speaker and the wall"? Is that the distance from the rear of the speaker or from the driver or the way sound has to pass around the speaker or...?
These may help too:

Frequency-Distance Calculator

Front Wall Absorption

--Ethan
Ethan Winer is offline   Reply With Quote
Old 26th February 2009   #25
Gear nut
 
Join Date: Nov 2007
Posts: 87

Seamus,

That fixed-frequency null will be present anywhere along the axis between the speaker and the listening position. That's what makes front wall nulls different from rear wall nulls, which change frequency as you move around the room. Front wall nulls, on the other hand, stay fixed in frequency as long as the listener is positioned so that the speaker is between the listener and the front wall.

Gernot,

Good question. I always use the voice coil position for my calculations. There's always a bit of rounding involved, but for bass freqencies, this amount of rounding is inconsequential.

--Wes
Wes Lachot is offline   Reply With Quote
Old 27th February 2009   #26
Gear addict
 
G. E.'s Avatar
 
Join Date: Feb 2009
Location: Austria
Posts: 431

Send a message via Skype™ to G. E.
Question Directivity vs. sound bending

Ethan,

don't you think that the directivity mentioned in the article is related to the speaker cabinets themselves (as opposed to the whole speaker) and sound waves from the speaker cabinets start bending around the speaker enclosure above a certain frequency? From my experience sound treatment (mid to high frequencies) of the front wall can make a huge difference -- personally I like putting up large diffusors (closed design) on the wall behind the speakers for those of us who have to stick with a non suffit-mount setup... Greets, Gernot
G. E. is online now   Reply With Quote
Old 27th February 2009   #27
Moderator
 
jayfrigo's Avatar
 
Join Date: Dec 2002
Posts: 3,352

Quote:
Originally Posted by G. E. View Post
personally I like putting up large diffusors (closed design) on the wall behind the speakers for those of us who have to stick with a non suffit-mount setup... Greets, Gernot
To get diffusion in the low frequency bands in question you'd need a sizable diffractal or a very deep 2D, neither of which is very plausible behind the speakers in a typical room; not to mention that you'd need to get quite a distance from it for it to truly be effective.

I tend to use a combination of trapping and broadband absorption behind the speakers when not soffiting. Even though infinite baffle (soffiting) solves some problems and looks great on paper, often free-standing monitors end up sounding better. They're certainly easier to fine tune after the room is built. Notice that in the vast majority of high-end mastering rooms the monitors are free-standing. Clearly both approaches can work well.
jayfrigo is offline   Reply With Quote
Old 27th February 2009   #28
Gear nut
 
davew's Avatar
 
Join Date: Mar 2007
Location: north and south
Posts: 142

i'm sure many of you will think this post is pure bull-turd! but a buddy of mine actually has 'part of a car,' with audio system in a room of his studio. no wheels, but indeed an enclosed car body with sound! sure saves time! thinking about doing the same!
__________________
Ribbon Foil
davew is offline   Reply With Quote
Old 27th February 2009   #29
Gear addict
 
G. E.'s Avatar
 
Join Date: Feb 2009
Location: Austria
Posts: 431

Send a message via Skype™ to G. E.
Lightbulb Front wall diffusion sounds good to me

Quote:
Originally Posted by jayfrigo View Post
To get diffusion in the low frequency bands in question you'd need a sizable diffractal or a very deep 2D, neither of which is very plausible behind the speakers in a typical room; not to mention that you'd need to get quite a distance from it for it to truly be effective...
Let me be more specific about upper mids/highs and front wall diffusor placement. For example setting up this diffusor (sorry, no better image available -- theoretical bandwith 1900Hz-2500Hz) instantly made THE most audible improvement ever for me (depth of the soundstage), I clearly preferred it over using absorbption. Btw: speakers have 3ft distance to the front wall, diffusor is a only few inches away from the front wall. Any explanations?

As for the low freq. response I really appreciate Wes' findings: some "problems" follow the speaker position only others depend on both speaker and listening position...
Attached Thumbnails
Changing Control Room Ratios (plus a parallel wall question)-front-wall-diffusor.jpg  

Last edited by G. E.; 27th February 2009 at 10:12 AM.. Reason: ... typos
G. E. is online now   Reply With Quote
Old 27th February 2009   #30
Lives for gear
 
Seamus TM's Avatar
 
Join Date: Aug 2004
Location: Upstate NY
Posts: 1,557

Thread Starter
Quote:
Originally Posted by Wes Lachot View Post
Seamus,

That fixed-frequency null will be present anywhere along the axis between the speaker and the listening position. That's what makes front wall nulls different from rear wall nulls, which change frequency as you move around the room. Front wall nulls, on the other hand, stay fixed in frequency as long as the listener is positioned so that the speaker is between the listener and the front wall.


--Wes
Crazy.
So, after I build the wall to change my length to 20.425, I would probably want to position the speakers in a place that makes that null higher in the frequency spectrum so that I could hit it with broadband absoption. Otherwise, if it's too low, I'd have to build some tuned traps...

does that even make sense...?

Thanks,
Seamus
Seamus TM is offline   Reply With Quote
New Reply New Reply Submit Thread to Facebook Facebook  Submit Thread to Twitter Twitter  Submit Thread to LinkedIn LinkedIn 



Thread Tools Search this Thread
Search this Thread:

Advanced Search

Similar Threads
Thread Thread starter Forum Replies Last Post
Guitarist in the Control Room..Amp in the Live Room question. Noize919 So much gear, so little time! 13 4th June 2008 07:11 PM
Parallel resistance calculation and changing a fader's value jsteiger Geekslutz forum 5 12th April 2008 01:36 AM
Vocals in the control room question dannygold High end 21 17th February 2008 04:06 PM
My Control Room Wall is Up! dbbubba So much gear, so little time! 5 26th November 2007 07:38 PM
Control Room Wall design lukejs So much gear, so little time! 13 13th March 2006 02:29 AM


All times are GMT +1. The time now is 04:01 AM.

 
 
Powered by vBulletin®
Gearslutz.com Limited - UK Company Number 7597610.
Registered Office: 35 Ballards Lane, London, N3 1XW.

SEO by vBSEO ©2010, Crawlability, Inc.