Old 4th January 2008, 03:46 AM   #1
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
How much power for studio...?

Howdy GS buddies!

Just bought a house with some very faulty wiring, so a call to an electrician is just a few days away. While he's here I'd like him to make sure I have enough dedicated, clean power. He'll be replacing the main trunk from the road to the house and installing a new breaker box ( I have two old ones... with screw-type fuses and electric chair -type throw levers...eeek!). I'd be happy to have a 2nd box just for the studio, if that might help......?

What does a typical, small-type, home studio need for power?

I'm recording mostly acoustic/americana/bluegrass and will have a DAW control room, vocal booth, and 4-5 other tracking booths. Each booth will need at least 2 outlets for tube mics and/or small amps (I know I said acoustic... but I can have a little fun too, eh?).

I'll be installing a dedicated HVAC so I'll need power for that too.

Anyone with any suggestions?

How much power do I need?????

THANKS!!!
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 4th January 2008, 05:33 AM   #2
DSD_Mastering
Lives for gear
 
DSD_Mastering's Avatar
 
Join Date: Nov 2006
Location: Seattle
Posts: 1,336
My basement studio is on it's own power with an Equi=tech 100amp wall cabinet. There are 2 dedicated circuits in each area of the studio. I don't ever see needing more power.

The Equi=tech website has formulas for calculating how much power you will need.

Regards,
Bruce
__________________
Bruce A. Brown
Puget Sound Studios
Seattle, Washington
DSD_Mastering is offline   Reply With Quote
Old 4th January 2008, 05:43 AM   #3
jdg
Lives for gear
 
jdg's Avatar
 
Join Date: Aug 2005
Location: seattle, WA
Posts: 1,128
100amp would be good to start unless ur getting a huge console and some tape machines.. then i would just start adding amps up.

i have two 20amp circuts, and no hvac. just daw, small amount of outboard, and lights. ... still have lots of juice left over.
__________________

panicStudios - mastering in seattle
jdg is offline   Reply With Quote
Old 4th January 2008, 03:01 PM   #4
nosebleedaudio
Lives for gear
 
nosebleedaudio's Avatar
 
Join Date: Jun 2005
Location: Birmingham, AL
Posts: 1,525
Send a message via AIM to nosebleedaudio
For tech power only one 20 amp will be plenty...
__________________
Mike Keith,
JMK Audio
www.jmkaudio.com
nosebleedaudio is online now   Reply With Quote
Old 4th January 2008, 03:39 PM   #5
Doublehelix
Lives for gear
 
Doublehelix's Avatar
 
Join Date: Jan 2004
Location: USA
Posts: 957
As part of my build-out, I added:

-20 amp circuit for the control room electronics (recording gear only) with star isolated ground
-20a for the live room
-20a for the iso room
-20a for the service plugs and lights
-20a for HVAC

-----

100 amps total
__________________
DH

"Nobody goes there anymore; it's too crowded."
-Yogi Berra
Doublehelix is offline   Reply With Quote
Old 4th January 2008, 04:27 PM   #6
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
Thank you'ns!

DSD, those Equitek systems are PRICY! Yeesh! Do you notice a huge difference between that an a standard Monster-type conditioner?

D-Helix are you completely satisfied with what you added... ie. would you do it any differently the second time around?

Thanks a BUNCH for your suggestions!!

-Mojo out!
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 4th January 2008, 07:56 PM   #7
DSD_Mastering
Lives for gear
 
DSD_Mastering's Avatar
 
Join Date: Nov 2006
Location: Seattle
Posts: 1,336
Quote:
Originally Posted by mojo1 View Post
Thank you'ns!
DSD, those Equitek systems are PRICY! Yeesh! Do you notice a huge difference between that an a standard Monster-type conditioner?
-Mojo out!
Yeah, I spent over $30k on electrical. The cabinet are about $10k and I'm using JPS labs in-wall cable and Oyaide R1 receptacles. The cabinet is tied with #4 copper wire to (2) 20' x 3/4" copper rods at 16' apart into the ground. I do have a couple of non-technical outlets in there and the difference is not subtle, even when using a Furman conditioner.

It's really a cumulative thing, where no one thing will make an audible difference, but putting them all together will make a major improvement. The difference can be heard mainly on amps and converters.

Regards,
Bruce
__________________
Bruce A. Brown
Puget Sound Studios
Seattle, Washington
DSD_Mastering is offline   Reply With Quote
Old 4th January 2008, 08:52 PM   #8
avare
Lives for gear
 
avare's Avatar
 
Join Date: May 2004
Location: Hamilton, On Canada
Posts: 948
This thread has been staying mostly on topic per the original post, so I will correct that.

If you are spending the money to do it right, what you may find more economical is to have the main audio power outlets wired with isolated grounds. Cheaper than balanced systems like what Equitech sells. Nothing negative about their products, but if you are doing wiring, isolated ground is cheaper. Isolated ground systems is a mature technology, and amongst the most common uses for it is in hospitals. Hospitals are not concerned about what something sounds like, they are concerned with saving lives. They do it right.

Living,
Andre
avare is online now   Reply With Quote
Old 5th January 2008, 12:22 AM   #9
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
Pardon my ignorance... isolated ground system... what's that?

I'm sure it has something to do with isolating the ground... but... um.... (I'm not an electrician and I don't even play one on tv!!).

Thanks for all of your help!

-Mojo
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 5th January 2008, 12:34 AM   #10
pan
Lives for gear
 
pan's Avatar
 
Join Date: Oct 2002
Location: Hamburg
Posts: 832
Send a message via AIM to pan
In a home-environment the Neutral is usually tied to Ground somewhere down the Line...

Isolated Ground means that you have a dedicated run for the Ground that is not connected to Neutral but directly connected to Earth - usually by a Groundpole.
__________________
Niko Sieveking

wot? no TR?
TSHAK k'BOOM
nichtlineareaudioproduktionen
pan is offline   Reply With Quote
Old 5th January 2008, 07:21 AM   #11
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
Seems easy... and logical...

So I should just tell my electrician about this and he'll know what to do? I'd like it done the right way, the first time!

Thanks again!

-Mojo
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 5th January 2008, 07:24 AM   #12
jammybastard
Gear nut
 
jammybastard's Avatar
 
Join Date: Oct 2005
Location: Tangyland USA
Posts: 87
when the power company showed up at my house for a service call and saw my studio and my 100amp service. they stayed and installed a 300 amp service.
__________________
Roll It! Take It! Media, LLC
jammybastard is offline   Reply With Quote
Old 5th January 2008, 07:46 AM   #13
jamsmith
Lives for gear
 
jamsmith's Avatar
 
Join Date: Dec 2007
Location: Atlanta, GA
Posts: 1,046
Quote:
Originally Posted by Doublehelix View Post
100 amps total
Assuming standard line voltages, that a capacity for 12,500 peak power.

You growing weed in there?

Grounding. Yes. Isolation. Isolation transformer if you can. Technically neutral and ground are the same thing - but in practice resistance can be found between them and that source of ground loop hum. This is what you do. Your breaker box has a grounding strip that you can run all the grounds too. Get a grounding rod - galvanized steel at least 8-10 ft long, 5/8 inches thick, drive that sucker in the ground and connect your grounding strip to that. This is called star grounding.

Extra nice ground: dig down a couple of feet before driving in rod. After the rod is inserted, pack some rock salt around the rod. Keep the ground moist. This is an old radio trick, probably over-kill for audio, but hell, it costs next to nothing.
__________________
Screamin' Michael Jamsmith - www.jamsmith.com

"You CAN polish a turd, but you just end up with a shiny turd."
jamsmith is offline   Reply With Quote
Old 5th January 2008, 02:31 PM   #14
nosebleedaudio
Lives for gear
 
nosebleedaudio's Avatar
 
Join Date: Jun 2005
Location: Birmingham, AL
Posts: 1,525
Send a message via AIM to nosebleedaudio
Quote:
Originally Posted by jamsmith View Post
Assuming standard line voltages, that a capacity for 12,500 peak power.

You growing weed in there?

Grounding. Yes. Isolation. Isolation transformer if you can. Technically neutral and ground are the same thing - but in practice resistance can be found between them and that source of ground loop hum. This is what you do. Your breaker box has a grounding strip that you can run all the grounds too. Get a grounding rod - galvanized steel at least 8-10 ft long, 5/8 inches thick, drive that sucker in the ground and connect your grounding strip to that. This is called star grounding.

Extra nice ground: dig down a couple of feet before driving in rod. After the rod is inserted, pack some rock salt around the rod. Keep the ground moist. This is an old radio trick, probably over-kill for audio, but hell, it costs next to nothing.
This is a BAD idea...and NOT to code..
Ground MUST be connected to the center tap of the main AC drop or you WILL not have a path for ground fault current, and will not trip a breaker.
A true dedicated ground means its connected at one point only and is a home run to the main panel, connected at the SAME point as neutral...
And salt is highly corrosive, drive more grounds rods...
__________________
Mike Keith,
JMK Audio
www.jmkaudio.com
nosebleedaudio is online now   Reply With Quote
Old 5th January 2008, 06:53 PM   #15
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
Hey Jammy!

Did they explain why they did that? Isn't that overkill? I'm up for it, just don't want to throw money away!!!!

Thanks!

-Mojo
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 7th January 2008, 05:32 PM   #16
mojo1
Gear nut
 
mojo1's Avatar
 
Join Date: Sep 2006
Posts: 133
Anyone...?
__________________
-Mojo
www.darkshadowrecording.com
www.stephenmougin.com

I got a fever...
mojo1 is offline   Reply With Quote
Old 7th January 2008, 05:42 PM   #17
nosebleedaudio
Lives for gear
 
nosebleedaudio's Avatar
 
Join Date: Jun 2005
Location: Birmingham, AL
Posts: 1,525
Send a message via AIM to nosebleedaudio
Let me say this another way, a better ground on the AC side will NOT compensate for a poorly designed piece of gear.
__________________
Mike Keith,
JMK Audio
www.jmkaudio.com
nosebleedaudio is online now   Reply With Quote
Old 7th January 2008, 06:34 PM   #18
plexisys
Gear addict
 
plexisys's Avatar
 
Join Date: Oct 2007
Location: A quite place
Posts: 407
Send a message via AIM to plexisys Send a message via Yahoo to plexisys
It's cheaper in the long run for the power company to put in a larger service than install just what is currently needed. They do not want to have to come back and reinstall a new box/service.

I've been talking with an electrical engineer about a new studio design. They recommend you get a service that is at least 3 times larger than your current need. You also have to keep in mind the spikes from AC and heating units every time they start up. This is as true for a home studio as it it is for a stand alone pro studio.
plexisys is online now   Reply With Quote
Old 10th January 2008, 06:30 AM   #19
jamsmith
Lives for gear
 
jamsmith's Avatar
 
Join Date: Dec 2007
Location: Atlanta, GA
Posts: 1,046
Quote:
Originally Posted by nosebleedaudio View Post
This is a BAD idea...and NOT to code..
Ground MUST be connected to the center tap of the main AC drop or you WILL not have a path for ground fault current, and will not trip a breaker.
A true dedicated ground means its connected at one point only and is a home run to the main panel, connected at the SAME point as neutral...
THIS IS A GOOD IDEA AND COMPLETLY UP TO CODE!

Technically correct: NEC does not permit isolation transformers to be installed in such a way to isolate the customers neutral from the utilities neutral. However, NEC does permit a "Separately Derived System" which a isolation transformer may create, providing 250.30 provisions are met. In a nutshell, NEC 250.30 provides that you can use an isolated transformer as long as you have "suitable grounding electrode" hence the "grounding rod". In all fairness, the grounding rod size and dimensions may not neccesarily fit the code for an particular installation. The actual size needed can be in found in NEC 250.66

Quote:
Originally Posted by nosebleedaudio View Post
And salt is highly corrosive, drive more grounds rods...
Yes, salt is highly corrosive that is the purpose for the galvanized steel.
__________________
Screamin' Michael Jamsmith - www.jamsmith.com

"You CAN polish a turd, but you just end up with a shiny turd."
jamsmith is offline   Reply With Quote
Old 10th January 2008, 02:14 PM   #20
nosebleedaudio
Lives for gear
 
nosebleedaudio's Avatar
 
Join Date: Jun 2005
Location: Birmingham, AL
Posts: 1,525
Send a message via AIM to nosebleedaudio
Quote:
Originally Posted by jamsmith View Post
THIS IS A GOOD IDEA AND COMPLETLY UP TO CODE!

Technically correct: NEC does not permit isolation transformers to be installed in such a way to isolate the customers neutral from the utilities neutral. However, NEC does permit a "Separately Derived System" which a isolation transformer may create, providing 250.30 provisions are met. In a nutshell, NEC 250.30 provides that you can use an isolated transformer as long as you have "suitable grounding electrode" hence the "grounding rod". In all fairness, the grounding rod size and dimensions may not neccesarily fit the code for an particular installation. The actual size needed can be in found in NEC 250.66



Yes, salt is highly corrosive that is the purpose for the galvanized steel.
Your confusing two different things, first I know section 250: and section 647: in the code book. My point was and STILL is all grounds have to be connected together at one point only or you will/can have a difference of potential between them, even if you use a iso trans...
IM a big fan of isolation transformers more so for balanced iso trans.
But a floating ground that is NOT connected is a bad idea.
It seems quite a few people have confused an isolated ground plug with an isolated ground, 2 totally different things.
Have been around AC for many years and have done my homework.
And if you need a better connection with the big ball of dirt "earth" then if it was me I would use 2 or more ground rods or a ground plate and connect all together.
And like I said the best ground connection to the earth will NOT compensate for poorly designed gear...
And I might have misread or added incorrectly to what your were saying, if I did.. Sorry..
It's just that this is a VERY important topic that has some giving wrong and dangerous advice...
Have seen many times someone states you need to disconnect the ground wires from the main AC ground, drive a separate ground rod and connect your ground wire to this, an isolated ground that DOES NOT accomplish anything and is dangerous...Safety first, hum/buzz can be corrected in other ways...
__________________
Mike Keith,
JMK Audio
www.jmkaudio.com
nosebleedaudio is online now   Reply With Quote
Old 10th January 2008, 08:23 PM   #21
jamsmith
Lives for gear
 
jamsmith's Avatar
 
Join Date: Dec 2007
Location: Atlanta, GA
Posts: 1,046
I never advocated a floating ground. I only advocation having a single ground, and all internal grounds connected to in a star methods. Every ground on every device directly to the one grounding point. And the grounding point be a single ground be one I have installed and know that there will be a single ground point. Why do I want to trust some municipal power company to ensure the ground they supply me with a proper ground? A "Separately Derived System" allow you to build an electrical system that give you complete control of your grounding.
__________________
Screamin' Michael Jamsmith - www.jamsmith.com

"You CAN polish a turd, but you just end up with a shiny turd."
jamsmith is offline   Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


All times are GMT +1. The time now is 03:26 PM.


Powered by vBulletin®
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.0.0