| | #1 |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | Help!!, 134 volts coming into my studio.
I recently had a power surge in my studio ( I believe it has to do with a large building that is under construction close to my home, or just the grid the house is on, although a blackout is not an uncommon thing in my area. ) I have all of my studio gear on 6 monster pro 2500 power strips, I was in the studio Thurs night when my entire room shut down, my power strips all read 134 volts in the led windows, at that voltage i cant turn on the gear even if I wanted to because the strips break at anything above 134 volts, the average reading now is 132 to 134, I have contacted my service provider to come check the grid and the service coming into my house etc, all of the outlets in my house are reading the same or similar high voltage. my question is : is it safe to run my gear at that voltage (not that I am going to) I just want to get the opinion of others who are familiar, or can suggest a long term voltage regulator that would be good for the studio. Thanks |
| | |
| | #2 |
| Lives for gear Join Date: Feb 2003 Location: Atascadero, CA
Posts: 4,035
Verified Member |
Do you have neighbors on the same electrical transformer but with different service lines? If so, take a measurement at their outlets. If they are not experiencing the same high voltage you may have a compromised "neutral" into your house. This needs to be sorted out ASAP. If the neighbor has the same high voltage coming down from separate lines then the provider needs to address the problem ( actually the provider needs to address this in either scenario). This may or may not be the issue but it sure was for me about a year ago and it took 3 service calls from PG&E before they found a loose neutral from the pole to my service box. My lights were flickering brighter than normal.....under most situations when lights flicker they go under normal brightness momentarily rather than over. My studio's heavy AC grounding scheme was keeping the AC drop from going completely ballistic but it was just a matter of time until 240 volts would have surged through the lines without a solid neutral. |
| | |
| | #3 | |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | Quote:
I'm waiting for my neighbor to come home now so I can check his service. This happened to me about two years ago after a blackout when they restored power, but the voltage slowly decreased over the course of a couple of days to normal, which for me is about 121 to 124. | |
| | |
| | #4 | |
| Mastering Join Date: Mar 2006
Posts: 3,099
| Quote:
BK
__________________ Bob Katz DIGITAL DOMAIN http://www.digido.com "There are two kinds of fools. One says-this is old and therefore good. The other says-this is new and therefore better." No trees were killed in the sending of this message. However a large number of electrons were terribly inconvenienced. | |
| | |
| | #5 |
| Lives for gear |
A couple of years ago we had the exact opposite problem. In the summer our voltage dropped to 90 volts. It turned out to be a very overloaded transformer that had seen better days. Our local electric utility is publicly owned and are very good at trouble shooting. They found the problem in less than an hour, had the transformer torn down and a new larger one installed in one afternoon and we have no had any problems since. We also had a problem with the lights flickering anytime there was any wind and that turned out to be a crimping problem at the pole and that too was also fixed in one afternoon. Surge voltages and over voltage problems are very damaging to equipment and should be fixed ASAP. It sounds like you are on the right path. I would not use any of your equipment until the problem is solved. If they cannot fix the problem in a short period of time you can purchase TOPAZ or other isolation transformers with a variable secondary so you can at least get the voltage to a safer level. Best of Luck!
__________________ -TOM- Thomas W. Bethel Managing Director Acoustik Musik, Ltd. Room with a View Productions Oberlin, OH 44074 www.acoustikmusik.com Doing what you love is freedom. Loving what you do is happiness. |
| | |
| | #6 |
| Gear addict Join Date: Nov 2006 Location: HI Ambacht, the Netherlands
Posts: 398
Verified Member |
We have 230v in the Netherlands, and i think in the rest of europe as well nowadays and i never heard of any problems here with over or under voltages, it's tight at 230v all the time. Is it some kind of USA thing then? maybe because of the bigger distances? Might be nice to know that some years ago (maybe even 10) we had 220v but the powercompanys turned it up really slowly (over a period of 3 or 4 years that is) to the 230v we have right now. Reason: transporting a higher voltage is easier and cheaper because you need less thicker cables to have the same amount of power (P = U x I > Watt = Voltage x Amperage). That is also the reason why they use these high voltages (380KV) to transport it over long distance > a LOT less thick cables = cheaper. So maybe they are slowly raising voltages as well in the states without telling people and they turned it up just a 'bit' to fast? |
| | |
| | #7 |
| Lives for gear |
Did you check it with a good VOM? 134V is not real high, about 10% over 120V, secondary on a transformer will have a 10% increase as well. Depends on the gear.... Would NOT want to see it any higher, 117V to 125V is a good margin.. Gear like Focusrite, ISA, Amek, Oram, runs hot on 120V, 134V would put it over the top... |
| | |
| | #8 | |
| Mastering Join Date: Mar 2006
Posts: 3,099
| Quote:
BK | |
| | |
| | #9 | |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | Quote:
Thanks for your suggestion about the Topaz, I am going to look into it since that was going to be my next post, What are the high end users doing to control the ac feeding the studio? I have complete access to my main panel, since I am renovating the basement now, everything is wide open and the studio is on the first floor, also on the plus side, I had the main service to the house replaced in 2004. I know the monster strips are not the best solution, but I am glad I have em and they did do what I would have wanted by shutting down. I'm going to look into the Topaz now and other high end units. Thanks | |
| | |
| | #10 | |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | Quote:
That may be the case, since converting to a high end room about 3 1/2 years ago, I have noticed voltage ranging anywhere from 121 to 124 on average, 126 would have been high. My gut tells me PSEG know whats going on, my only concern is to protect my investment at this point. | |
| | |
| | #11 | |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | Quote:
| |
| | |
| | #12 |
| Lives for gear |
I looked at an old MCI manual, JH-110C made in the early 80's, its specs are; 115V +-10%... So from 103.5V to 126.5V... The machine will work just fine under those levels... For gear in the USA I have seen 117V specs MANY times... How many times do you think people have high or low voltage and DON"T even know it, better to know, just making a point... |
| | |
| | #13 |
| Gear maniac Join Date: Mar 2006 Location: Chicago
Posts: 194
|
For your entire facility, consider a Sola Hevi Duty MCR - a lot of $$ but does the job. Otherwise, enough Furman Voltage Regulators (AR-15 II etc.) to cover all of your circuits. I have survived several electrical events thanks to these (brownouts and lightning strikes). One lightning strike took out the only two things in my studio that did not have a Furman in line. However, 134 V is getting close to the 137 V maximum input of the Furman.
__________________ [k]ƒ |
| | |
| | #14 |
| Gear maniac Join Date: Dec 2007 Location: Pennsylvania
Posts: 247
|
To the OP, First, it would really help to know what country you are in. Depending on what type of overvoltage protection your power strips use, eg carbon block, gas tube, etc, if you experienced an overvoltage that shut everything down, then that protection could easily have been destroyed/compromised in the event. So I wouldn't trust them to protect your gear again until you've had them tested. As to what can or can't survive is a crap shoot at best. Smaller devices with switching power supplies could care less about input voltage, while conventional supplies are more at risk. I once worked a show where the idiot electrician had reconnected stage power (after some wack audience members had yanked it out in some bizarre tug of war) so all the 120 lines were hot with 220. All the PA's Crown amps cruised along fine, but their BGW's all popped and went south. You may want to look into some of the excellent UPS's that are available that output a sine wave. These are honestly your very best bet as to conditioning and regulating the power. You don't have to put everything on them, just the really critical stuff. Good luck!
__________________ "Yes, I know what I'm talking about, but that doesn't mean I'm right." -Randall Thomas |
| | |
| | #15 |
| Gear addict Join Date: May 2005
Posts: 496
Verified Member |
When I bought my first "real" piece of gear, I also bought a Furman AR-1215. Everything runs @ +/- 3 volts at 120 VAC in my space. I sleep better at night.
__________________ Cass Anawaty, Chief Engineer Sunbreak Music, LLC High Resolution Stereo Mastering www.sunbreakmusic.com |
| | |
| | #16 |
| Lives for gear | Wide Goalposts
I had flickering lights when I first moved here. Turned out there was a steel smelting plant. Irish Steel in the Harbour, flickering the whole city! EU mains seems to be settling at 230V. Mine was 235-240. I contacted the supplier. Their contract which I never read, stipulates 190-250V as good! I would take US voltage to be nominally 117, so 134 doesn't seem outrageous to me. DD |
| | |
| | #17 | |
| Lives for gear Join Date: Aug 2003 Location: Hollywood CA
Posts: 2,611
Verified Member | Quote:
DC | |
| | |
| | #18 | |
| Gear nut Join Date: Jan 2008
Posts: 100
| Quote:
Dave P. | |
| | |
| | #19 |
| Lives for gear Join Date: Apr 2004 Location: Virginia
Posts: 1,370
|
Please forgive me if this sounds silly, but an entry level regulator only costs about $400. Sometimes mine (furman AR1215) causes problems with some gear, I still feel a little better having it in the chain.
__________________ www.symphonicsound.com "The secret of life, though, is falling down seven times and get up eight times." Paulo Coelho |
| | |
| | #20 |
| Lives for gear |
You can get a very large autoformer/variac for very little money and set your own output level. It is not automatic but they do make some and every once in a while you see them up for sale. Check this place out. HGR Industrial Surplus - We sell everything and HGR Industrial Surplus - We sell everything |
| | |
| | #21 | |
| Lives for gear | Quote:
Also where exactly did you get that reading? At the panel? At an outlet? | |
| | |
| | #22 | |
| Lives for gear Join Date: Oct 2008 Location: Espoo Finland
Posts: 854
| Quote:
| |
| | |
| | #23 |
| Lives for gear Join Date: Sep 2006 Location: Rio de Janeiro, Brazil
Posts: 4,043
Verified Member |
At this point, my studio is getting 125v from the outlet... and that has been an average for the past 10 years... i would risk to say that up to 127v it is still normal, i have seen voltage peaks of over 130v, especially at the end of the afternoon when close by factories shut off their machinery.. ... Everything i have in the studio passes through a fairly big UPS and receives 117v, though (except the power amps and AC)
|
| | |
| | #24 | |
| Mastering Join Date: Mar 2006
Posts: 3,099
| Quote:
Anything over 120 gives me pause regarding the long term life of our gear. A lot of audio gear is just linear supplies. BK | |
| | |
| | #25 | |
| Lives for gear | Quote:
5% over that is 126V, that would be just fine... Like I mentioned above MCI's specs were +-10%, for a linear supply... ANY supply that can not handle 126V is a piece of crap in my book... | |
| | |
| | #26 | |
| Mastering Join Date: Mar 2006
Posts: 3,099
| Quote:
Anyway, you're probably right, Mike. But how comfortable do you feel in terms of rating the MTBF (mean time between failures) of a linear supply being fed 126 volts all day, every day, over time, versus 120? If the supply is rugged and well made, perhaps they are equivalent. But heat does take its toll, and I wager the internal temperatures will be measurably higher at 126 than 120. BK | |
| | |
| | #27 | |
| Lives for gear | Quote:
But the fact is AC power will never be the same (voltage) everywhere all the time... Have had to modify many under designed supplies that ran VERY hot from 120V...NOT 126 or more... It may sound like IM saying over voltage is NOTHING to worry about, it should not be MOST of the time... Will add that if I was involved in a studio that had around 126V most of the time and had ANY peaks that went much over that I would look into it... | |
| | |
| | #28 | |
| Lives for gear Join Date: Aug 2003 Location: Hollywood CA
Posts: 2,611
Verified Member | Quote:
It's a bit tricky, as running 5% high does not make the supply 5% less reliable! DC | |
| | |
| | #29 |
| Gear addict Join Date: May 2006
Posts: 331
Thread Starter | back down to 122-124
Today the average is backdown to 122-124, Back to work for me! ![]() Thanks Guys |
| | |
New Reply
Facebook
Twitter
LinkedIn
| Thread Tools | Search this Thread |
| Similar Threads | ||||
| Thread | Thread starter | Forum | Replies | Last Post |
| liability document for a freelance engineer&client coming to my studio? | lord_bunny | Studio Business | 3 | 7th February 2009 08:18 PM |
| 110-220 volts in, 5 volts out.... ok in Europe? | Firefox | So much gear, so little time! | 4 | 24th March 2008 11:59 AM |
| 002 R 110 Volts to 220 Volts switch? | BruceTheProduce | Geekslutz forum | 7 | 1st July 2007 08:34 AM |
| ATM450's for $134 NEW!!! | drummerboy1533 | So much gear, so little time! | 1 | 7th March 2007 04:33 AM |
| How many volts are 13 dBu? | bobby_z | Geekslutz forum | 10 | 10th May 2006 11:20 PM |
| |