New building, balanced power, grounding question...

Thread Tools Search this Thread
Old 18th December 2002   #1
Lives for gear
 
cajonezzz's Avatar
 
Joined: Jun 2002
Location: Carlsbad Ca.
Posts: 1,765

Thread Starter
Send a message via AIM to cajonezzz Send a message via MSN to cajonezzz Send a message via Skype™ to cajonezzz
New building, balanced power, grounding question...

Hi all, we've started the build out of our new facility. It's an old wharehouse that has gone through numerous tenants , the most recent being an upholstery shop.
We've planned on putting Equitech balanced power in both the control A and edit room to power all audioas well as the power to various stuff that will be plugged in the main room.

Question is the integrity of the ground to the building itself. I haven't been able to track down the existing ground (probably a water main but I haven't found it yet)
How would one go about determining if the building has a good ground? Is there an easy method to check this out or should we just go ahead and sink a new ground for good measure. This is new to me, thanks for the help.

oh, and pictures of the building in progress to follow if anyone is interested.
__________________
http://recordingdrummerproducer.com
http://socaldrumsociety.com
http://ProCraftMedia.com


-----------------------------------------------------------------
Watch your thoughts, for they become words.
Watch your words, for they become actions.
Watch your actions, for they become habits.
Watch your habits, for they become character.
Watch your character, for it becomes your destiny.
cajonezzz is offline  
Old 18th December 2002   #2
Gear maniac
 
Joined: Jun 2002
Location: So Cal
Posts: 166

Nothing beats having your electrician put a 6' copper rod into terra ferma. Talk to the guys who'll be doing the rewiring, they'll know the amount of potential each rod can displace, you'll need several.
Tubelover is offline  
Old 18th December 2002   #3
Lives for gear
 
subspace's Avatar
 
Joined: Jun 2002
Location: Too sun
Posts: 860

If you're doing any exterior landscaping, flowerbeds make great places for a row of ground spikes. Daily watering can really enhance the ground potential.
__________________
"If you never did, you should. These things are fun and fun is good."
subspace is offline  
Old 18th December 2002   #4
Lives for gear
 
atticus's Avatar
 
Joined: Nov 2002
Location: Ohio
Posts: 1,581

I had a chance to spend a day visiting Sear sound and Walter showed me that he has several turns of #2 welding cable encircling the studio and control room with all of the equipment grounds being tied into that. Sear sound is on the sixth floor of a building in Manhattan so I can se why he'd like to "self-ground" rather then using Con-Ed's.
__________________
David Seymour
Analog Audio Works
330-354-1576
atticus is offline  
Old 18th December 2002   #5
Gear maniac
 
Joined: Jun 2002
Location: So Cal
Posts: 166

Quote:
...with all of the equipment grounds being tied into that.
And then to what ?

It's not a ground if it doesn't find the real ground, as in the earth. I'm sure the guy knows what he's doing, but there must be more to it.
Tubelover is offline  
Old 18th December 2002   #6
Lives for gear
 
atticus's Avatar
 
Joined: Nov 2002
Location: Ohio
Posts: 1,581

Got me, man! He quickly went on to showing me his collection of the coolest mics in the world and his Fairchilds as well as his Neve and Avalon consoles and I don't remember thing one about the rest of the ground path. Sorry
atticus is offline  
Old 18th December 2002   #7
Lives for gear
 
sonic dogg's Avatar
 
Joined: Jul 2002
Location: pacific northwest
Posts: 872

Is this a building that has now or has had multiple tenants? There will be a room dedicated to the Main Service of the building...out of which could be any number of Feeders supplying panels of different sizes and possibly different voltages/phases etc....in this dedicated room will be the Service Grounding conductor....and a clue as to what type of ground they have available in the building....there will be a water ground of some sort though if the interior water pipe system is in pvc then the ground will only be to ground any metal parts at the drinking fountains...mop sinks ect...there will likely be suplemental grounds...ie. building steel,ground ring,ground rod(which should be a minimum of 10'..per code)something of this ilk....whoever your electrician is doing your install, its good in your situation, to have someone familiar with sound circuitry and isolation...your basic housewireman may not have enough experience with this to get it all quiet and safe too..........peace
__________________
the clubhouse studio....home of drool'n dogg rekords
sonic dogg is offline  
Old 19th December 2002   #8
Lives for gear
 
Steve Smith's Avatar
 
Joined: Jun 2002
Location: Chicago, IL
Posts: 1,384

ditto to all the above, drive a new rod(s).. and congrats on the Equitech, works great.. mine is my most favorite piece of gear!
__________________
Steve Smith - Unorignal, yet commonplace.
Steve Smith is offline  
Submit Thread to Facebook Facebook  Submit Thread to Twitter Twitter  Submit Thread to LinkedIn LinkedIn 



Thread Tools Search this Thread
Search this Thread:

Advanced Search

Similar Threads
Thread Thread starter Forum Replies Last Post
Newbie power distro questions. Spettitt3 Remote Possibilities in Acoustic Music & Location Recording 10 6th August 2007 04:40 AM
balanced power/power conditioning question for home studio construction pentajigga Bass traps, acoustic panels, foam etc 24 27th December 2006 03:17 PM
Balanced power and UPS ? cppi Remote Possibilities in Acoustic Music & Location Recording 4 24th May 2006 03:08 PM
Balanced Power / dimmer question KurtR Geekslutz forum 4 18th October 2005 09:34 PM
Balanced power, grounding etc... Seti808 High end 23 7th October 2005 03:30 PM


All times are GMT +1. The time now is 11:29 PM.

Home - Search Forum - Contact Us - Terms Of Use - Advertise on Gearslutz - All Advertisers - Archive - Top
 
 
Powered by vBulletin®
Gearslutz.com LTD - UK Company Number 7597610.
Registered Office - 35 Ballards Lane, London, N3 1XW.
Hosted by Nimbus Hosting.

SEO by vBSEO ©2010, Crawlability, Inc.